In this all-technical three-hour seminar, Dan Holohan will give you a Liberal Arts education in those Classic Hydronics systems. He’ll have you seeing inside the pipes as...
When servicing old hot-water heating systems that originally circulated by gravity, but now use circulating pumps, I began to notice a lot of oversized circulators. In some cases, the circulator was so severely oversized that the boiler could hardly get any heat out to the radiators. The water couldn't pick up much heat in the boiler or shed it in the radiators because it was moving so fast. There is very little resistance in the large pipes of a gravity system, so the consequences of oversizing the circulator are more severe than in a newer system with smaller pipes.
Looking for some way to determine the proper circulator size, I got hold of a copy of the Bell & Gossett Handbook from the 1940s and a Taco catalog which has no date on it, but appears to be a bit newer than the B&G book. Both tell you to use the next size larger circulator on a gravity conversion. Doing the math, I determined that both manufacturers were essentially saying to use a circulator about 50% larger on a gravity conversion than on a newer system designed for forced circulation. This is because of all the extra water contained in the larger pipes of a gravity system.
The resulting chart gives the circulator size in Gallons per Minute (GPM) for a hot-water system according to how many thousands of BTUs (MBH) or radiator square feet (EDR) the system is designed for. It gives the results for the usual forced-circulation system as well as for a gravity conversion. Besides using the chart to select circulators for a new system or boiler replacement, a technician can take this chart into the field to help troubleshoot a system that's not heating properly.
When replacing a boiler, don't hesitate to not use the circulator that came with the boiler if it's not the right size for the job. Packaged boilers are nice, but one size of circulator can never fit every job. Size your circulator properly and the system will run much better.
How to Use the Chart
You will need to have the performance charts, also called pump curves, of the circulators you're going to use. These should be available from your supplier or manufacturer's representative. If you have trouble getting these performance charts, or if you're looking for a chart for an older circulator, contact Dan Holohan.
Notes:
Choosing the Proper Circulator for a Converted Gravity Hot-Water System
The following information is taken from the various circulator maker’s performance charts showing the flow rates for their products at a head (back-pressure) of 3-1/2 feet. This accounts for the resistance in the boiler, near-boiler piping, flow-check (if used) and air separator. The system piping was designed to facilitate gravity circulation so we don’t need that much help here from the circulator. All we need is to approximate the rate of gravity flow when the original boiler was at its maximum design temperature of 180 degrees F.
After you have measured the existing radiation (and allowed a bit extra if radiators have been removed) take the EDR total to the chart below. Try to pick a circulator that is closest to your radiation without going under or too far over the total radiation. This will assure that the system will have at least 10 degrees delta-T (temperature differential) between flow and return.
I’ve included standard iron-body, flange-mount, lower-head units from the three most popular circulator manufacturers in America, in alphabetical order: Bell & Gossett, Grundfos and Taco. If you prefer to use another brand, just check its performance chart for flow rate at 3-1/2 feet (or 1 meter) of head. If you’re using metrics, multiply gallons per minute by 3.78 to convert to liters per minute.
Circulator Make & Model GPM at 3-1/2 Feet of Head EDR on Gravity Conversion
(Shown as Circulator Model Number, GPM, Maximum EDR)
Bell & Gossett NRF series
NRF-9/LW 7.5 320
NRF-22 17 725
NRF-33 27 1151
Bell & Gossett PL series
PL-30 27 1151
PL-50 47 2004
Bell & Gossett LR series
LR-20BF 16 682
Bell & Gossett three-piece Boosters
100 27 1151
HV 37 1578
2-inch 62 2643
Grundfos UP series
15-10F 5 214
15-42F 13 554
15-58F (high speed) 17 725
26-64F 27 1151
43-75F 41 1748
50-75F 41 1748
Taco “00" series
005 17 725
007 19 810
0010 30 1279
0012 45 1919
Taco 110 series, three-piece
110 27 1151
111 45 1919
120 60 2558
(You'll find Steamhead HERE.)